| ??? 09/21/06 00:45 Read: times  | 
#124733 - I've done a bit of this.... Responding to: ???'s previous message  | 
You probably wouldn't put modbus tcp/ip in your microcontrollers. You would probably use fibre optic ethernet for the backbone between floors of a building and use modbus tcp/ip -> RS485 converters on each floor and run copper to your controllers. You controllers would run modbus RTU. I've not done Much with BacNet but I would suspect it would be similar - most thigs run an ethernet backbone these days.  | 